yesterlectric
Senior Member
- Location
- Texas
- Occupation
- Electrician
There’s a difference of opinion regarding what should be required/allowed for proper isolation for deenergized work. The situation involves replacing a feeder breaker in a panelboard in a circumstance where due to choices in design, a complete outage on the entirety of the panelboard requires shut down of the customer owned substation and all customer loads. I have a couple of questions:
- If these panelboards have line side “barriers” (which are really just a form of insulation and sometimes imperfect at that ) as required by NEC section 230.62 and 215.15, is it nolonger considered “energized electrical work” to just open and lock the main breaker, test, and then remove the covers to do the work on the load side?
- Has OSHA ruled or issued any opinions on whether it’s considered infeasible to expect the line side of the panelboard to be the energized for work on it slow side? In most cases where this scenario comes up, it’s the fact that you have to get the utility out to deenergize. In this case, it’s the fact that due to choices in design, the customer has to experience a complete substation outage.