what article in the nec prohibits bonding the nuetral in subpanels?

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
Welcome Steve.

250.24(A)(5) Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
steveng said:
i am looking for the nec article on subpanel wiring methods?
thanks for any help.

The term "subpanel" is not used in the NEC. For Panelboards, see Article 408.

For wiring methods, see Chapter 3. Chapter 3 is all the Articles in the three-hundreds. Article 300 gives you general rules that apply to all wiring methods, 310 gives you information about conductor ampacities.

The most effective way to use the code in this instance is to determine what wiring method you would like to use, and then refer to it's specific article to see if you can use it.

For example, if I wanted to run a 60A "subpanel" in a dwelling unit in NM cable, then I would refer to Article 334 to determine if I could, and what rules surround it's installation. The same setup in a large commercial building would likely be illegal in NM.
 

iwire

Moderator
Staff member
Location
Massachusetts
georgestolz said:
Heh heh - after looking at the title of the thread, I understand why Bob had focused solely on bonding! :D :D

I was wondering what I missed. :D

But I do agree with all your other points anyway. :cool:
 

steveng

Senior Member
Location
Texas
thanks for the help!

thanks for the help!

one thing i like about this forum is you can get answers to difficult questions.

i had one more question:

sirs, i was changing out a light switch in my house
and i measured the voltage from hot side to the bare copper ground wire, and only got 86volts, when i measured the other side of the switch leg, i got 27 volts,
anyone have an explanation.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
steveng said:
sirs, i was changing out a light switch in my house
and i measured the voltage from hot side to the bare copper ground wire, and only got 86volts, when i measured the other side of the switch leg, i got 27 volts,
anyone have an explanation.
Yes, the circuit breaker was still on. By shutting off the circuit breaker, you don't risk a shock when replacing the switch. ;)

Kidding aside, the 27V I can explain, but the 86V is a mystery to me.

What kind of switch was there: Threeway, single pole, dimmer?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
georgestolz said:
Kidding aside, the 27V I can explain, but the 86V is a mystery to me.
The 86 volts is a mystery especially since my tester will often read 86 volts on a 120 volt circuit. I know it is my tester but the fact that you are reading 86 makes me think you may have the same problem with the tester as I do. Often I just need to retest and I get 120 + or -.
If there is a dimmer on the circuit you may get some reading through that hence the 27 v. Is that what you were thinking George or is there something else.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Dennis Alwon said:
If there is a dimmer on the circuit you may get some reading through that hence the 27 v. Is that what you were thinking George or is there something else.
I was thinking the 27v could have been induced voltage on a de-energized traveller.
 
steveng said:
one thing i like about this forum is you can get answers to difficult questions.

i had one more question:

sirs, i was changing out a light switch in my house
and i measured the voltage from hot side to the bare copper ground wire, and only got 86volts, when i measured the other side of the switch leg, i got 27 volts,
anyone have an explanation.
I would look for a broken neutral. I had the same readings on a 3 way that had a broken neutral in one of the switch boxexs
 

jeff43222

Senior Member
What kind of tester are you using? I've read as much as 120V of induced voltage with my Fluke. Make sure you are using a high-impedance tester. That 86V could be induced, or, like the others have said, it could be due to a loose neutral somewhere.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Jeff,
Make sure you are using a high-impedance tester.
If you are trying to eliminate the effects of induced or ghost voltage, you need a low impedance tester...something that has enough load to draw this voltage down so the tester does not read it.
Don
 

steveng

Senior Member
Location
Texas
jeff43222 said:
What kind of tester are you using? I've read as much as 120V of induced voltage with my Fluke. Make sure you are using a high-impedance tester. That 86V could be induced, or, like the others have said, it could be due to a loose neutral somewhere.


fluke TI600 , thanks for the help
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Fluke has a new stray voltage adapter, it plugs into your DMM and it must load the circuit. Also there new 117 has a Lo-Z function and built in Volt Alert.
 