250.24(A)(5) Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.
steveng said:i am looking for the nec article on subpanel wiring methods?
thanks for any help.
georgestolz said:Heh heh - after looking at the title of the thread, I understand why Bob had focused solely on bonding!
Yes, the circuit breaker was still on. By shutting off the circuit breaker, you don't risk a shock when replacing the switch.steveng said:sirs, i was changing out a light switch in my house
and i measured the voltage from hot side to the bare copper ground wire, and only got 86volts, when i measured the other side of the switch leg, i got 27 volts,
anyone have an explanation.
The 86 volts is a mystery especially since my tester will often read 86 volts on a 120 volt circuit. I know it is my tester but the fact that you are reading 86 makes me think you may have the same problem with the tester as I do. Often I just need to retest and I get 120 + or -.georgestolz said:Kidding aside, the 27V I can explain, but the 86V is a mystery to me.
I was thinking the 27v could have been induced voltage on a de-energized traveller.Dennis Alwon said:If there is a dimmer on the circuit you may get some reading through that hence the 27 v. Is that what you were thinking George or is there something else.
I would look for a broken neutral. I had the same readings on a 3 way that had a broken neutral in one of the switch boxexssteveng said:one thing i like about this forum is you can get answers to difficult questions.
i had one more question:
sirs, i was changing out a light switch in my house
and i measured the voltage from hot side to the bare copper ground wire, and only got 86volts, when i measured the other side of the switch leg, i got 27 volts,
anyone have an explanation.
If you are trying to eliminate the effects of induced or ghost voltage, you need a low impedance tester...something that has enough load to draw this voltage down so the tester does not read it.Make sure you are using a high-impedance tester.
jeff43222 said:What kind of tester are you using? I've read as much as 120V of induced voltage with my Fluke. Make sure you are using a high-impedance tester. That 86V could be induced, or, like the others have said, it could be due to a loose neutral somewhere.