220215-1057 EST
I am supplied on the pole with a three phase delta. My entire block has about 28 homes, and almost all are single phase. The homes are about equally distributed on the three supply lines. My home on the block is the first load on that supply. Across the street from me a tree branch came down breaking only one primary wire. Thus, the block was fed with a single single phase source.
What happened? All homes connected to that single phase source had no interruption of power. But 2/3 of the homes had their transformers connected in series, and these seriesed transformer were shunted across the working single phase source. All the homes have refrigerators and freezers, and possibly some other similar loads ( motors with built in overload protection ).
A motor would receive inadequate voltage, not start, putting a load on the system, and after a short time trip out removing its load for some short time, and then reclose. Each motor was random in its timing. Thus, voltage fluctuated between about 10 to 20 V, and 90 to 100 V on the homes with the primary wire that was broken.
This would not happen on a wye source. Just one phase would be lost, and it would be completely dead. However, I like and prefer my delta source.
.