paul hodge
Member
- Location
- atl
What is the defining line between a feeder and a branch circuit?
LarryFine said:And for the thread-busting question, does an OCPD (such as an AC disco) at the end of a branch circuit change that circuit into a feeder?
(I say no.)
Are you sure?Pierre C Belarge said:If an individual chooses, for whatever reason, to install a disco with fuses or a circuit breaker at the location of the AC unit, then the conductors between the panel and the fused disco are feeders.
The NEC refers to this overcurrent protection existing at the end of a branch circuit.Supplementary Overcurrent Protective Device. A device intended to provide limited overcurrent protection for specific applications and utilization equipment such as luminaires (lighting fixtures) and appliances. This limited protection is in addition to the protection provided in the required branch circuit by the branch circuit overcurrent protective device.
Agreed.I do not see any reason why it would impact the installation other than being a technicality.
Do you have one in particular in mind?A supplementary device is not designed the same as a standard overcurrent device. Take a look at some of the websites that provide this info.
It is a huge impact if the conductors to the fused AC disconnect are feeders, because if they are feeders they have to sized to the rating of the feeder OCPD. If they are branch circuits they are sized to the minimum circuit size shown on the nameplate and the branch OCPD can be sized per the maximum OCPD shown on the name plate. In many cases, if the conductors are feeders, they would have to be two sizes larger than if they are branch circuit conductors. It is my opinion that the fused disconnect at the AC unit is not the branch circuit OCPD.I do not see any reason why it would impact the installation other than being a technicality.
--------------------------------------------------------------------------------
Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).
Feeder. All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device.
__________________
Bob
--------------------------------------------------------------------------------
And for the thread-busting question, does an OCPD (such as an AC disco) at the end of a branch circuit change that circuit into a feeder?
(I say no.)
__________________
Larry B. Fine
tom baker said:Along Dons comment "It is my opinion that the fused disconnect at the AC unit is not the branch circuit OCPD."
If the fused disco was a feeder then it would require a grounding electrode system, if it was outside the building, and I have not seen that done.
Its a maintenance disconnect or supplemental OCD. In fact, regarding light poles, there was a code change a few years ago to clarify that light poles are not buildings and don't require disconnects. See 225.32 Ex 3
jim dungar said:There is no requirement in Article 215 for a "grounding electrode system" just because the circuit is a feeder that is outdoors. Of course, if the device is also a "building disconnect" then other NEC articles may be applicable.
Yes, but a seperate "structure" does require a grounding electrode system, and per the NEC just about everything is a structure. If the conductors serving the structure are branch circuit conductors, then the exception to 250.32(A) says you do not need the grounding electrode sytem. If the conductors are feeder conductors, then you do.There is no requirement in Article 215 for a "grounding electrode system" just because the circuit is a feeder that is outdoors. Of course, if the device is also a "building disconnect" then other NEC articles may be applicable.