What determines service size?

Status
Not open for further replies.

VoltageHz

Member
Location
NJ
Is there a universal specification that determines the size of a service across many different situations?

If you have the service entrance conductors sized for 200 Amps and the meter pan rated for such, but the main panel has a 150 Amp breaker, what size service is that?

If you have a service in a multi-family house with multiple panels with different size main breakers, how to determine that size service?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Is there a universal specification that determines the size of a service across many different situations?
For the minimum service for a specific premises, you need to do load calcs. For a given service, the weakest link is the limit.

If you have the service entrance conductors sized for 200 Amps and the meter pan rated for such, but the main panel has a 150 Amp breaker, what size service is that?
It sounds like a 150a service that could be upped to 200a to me.

If you have a service in a multi-family house with multiple panels with different size main breakers, how to determine that size service?
The limiting factor in the main service is, well, the limiting factor. Is there a main for the building?
 

VoltageHz

Member
Location
NJ
For the minimum service for a specific premises, you need to do load calcs. For a given service, the weakest link is the limit.

It sounds like a 150a service that could be upped to 200a to me.

The limiting factor in the main service is, well, the limiting factor. Is there a main for the building?

I'm speaking speculative here, curiosity only.

So the main breaker alone is what determines the service size?

What if there are multiple main panels (each fed with it's own meter) with different size main breakers?
 

Rewire

Senior Member
Services are sized to the calculated load. The service for a multi family dwelling is calculated based on the load of each dwelling applying appropiate demand factors.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
What if there are multiple main panels (each fed with it's own meter) with different size main breakers?

It would be whatever kw the meter stack is rated for. you wouldn't necessarily rate the service as the sum of the rating for each disconnect.
 

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
You don't size the service. You size the conductors, you size the conduits, you size the overcurrent protection. You don't size the service.
 

iMuse97

Senior Member
Location
Chicagoland
I'm speaking speculative here, curiosity only.

So the main breaker alone is what determines the service size?

What if there are multiple main panels (each fed with it's own meter) with different size main breakers?

1. multiple panels with separate meters could be multiple services; I've done work at a building with several laterals/drops to the facility.

2. the weakest link determines the service size, and then the main OCPD must be sized to protect that weakest link.
 
Last edited:
First, the number of services is determined by the number of laterals or service drops.


A single service drop can supply more than one set of service entrance conductors. Each set of service entrance conductors can serve up to 6 disconnecting means.


If there is 1 service disconnecting means, the size of the service is generally determined by the rating of the single disconnecting means and sized according to 230.42.



There may be multiple service disconnecting means supplied from one service drop. The size of the conductors supplying the multiple disconnecting means is per 230.90 ex #3.

At this point, I have heard all kinds of electricians call the size of the service all kinds of numbers.

You may have 2 sets of 500Kcmil supplying 5 sets of 200A rated disconnecting means. Some may call it an 800A service. Although the load may actually be less than 800A.
 

satcom

Senior Member
I my town many of the utility drops are #10 open air and when someone upgrades their service to 200A the service drop stays.
 