What determines the service size? Breaker or conductors?

ryangittens

Member
Location
usa
NEC 2017, 2014 references service size for the max supply side connection OCPD.

If the wires support a larger amperage than the main breaker would it be appropriate to use the conductors as the service size so we can use a bigger OCPD for the solar than the main?
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
While 2017 NEC 705.12(A) refers to the "rating of the service," in the 2020 NEC, 705.11(A) clarifies this to "ampacity of the service conductors."

So since both physics and the 2020 NEC wording indicate that "rating of the service" means the ampacity of the conductors, not the service OCPD size, then I'd say that would be the proper interpretation for the 2017 NEC.

Cheers, Wayne
 

pv_n00b

Senior Member
Location
CA, USA
I would go by not only the size of the service entrance conductors but also the service rating that the utility has provisioned the site for. I've been bitten before when sizing a system based on the customer service equipment size only to find out the utility has installed a smaller service transformer than the service conductors might imply. Upsizing the utility transformer was not an option so the system size had to be reduced.
 

ryangittens

Member
Location
usa
While 2017 NEC 705.12(A) refers to the "rating of the service," in the 2020 NEC, 705.11(A) clarifies this to "ampacity of the service conductors."

So since both physics and the 2020 NEC wording indicate that "rating of the service" means the ampacity of the conductors, not the service OCPD size, then I'd say that would be the proper interpretation for the 2017 NEC.

Cheers, Wayne
Thank you
 

ryangittens

Member
Location
usa
I would go by not only the size of the service entrance conductors but also the service rating that the utility has provisioned the site for. I've been bitten before when sizing a system based on the customer service equipment size only to find out the utility has installed a smaller service transformer than the service conductors might imply. Upsizing the utility transformer was not an option so the system size had to be reduced.
Thank you
 