kolyan2k
Member
- Location
- United States
Since I think many or most have double-insulated motors, do you just run it from cu pipe and coil it up, dont run it at all, or run from pipe to outlet EGC?
Read 680.74. Pretty easy.Since I think many or most have double-insulated motors, do you just run it from cu pipe and coil it up, dont run it at all, or run from pipe to outlet EGC?
Read 680.74. Pretty easy.
No, you don't take it to an outlet egc.
Well strike me down. :ashamed1:from 680.74....."...Bonding jumper shall be provided and shall be terminated to EGC of branch circuit of the motor..."