This is my first time posting on here guys, so please forgive me if I happen to post this in the wrong place, or just plain wrong...:?
Recently I was faced with a installation that involved a 3/4" EMT conduit connecting a outlet in a office to a juction box in the drop ceiling. The conduit is installed in a concrete filled non-moisture subjected block wall that separates offices inside a wherehouse. The conduit was cut too close to wall and right at the the pipes bending radius making it impossible to put a EMT connector on as to attach it to the 4 square junction box. Since the wall is block, and the EMT conduit is set in concrete, the only option I could see to do, minus cutting & jack hammering concrete and making a huge mess, was to install a hammer-on plastic bushing and put the 4 square box over the conduit, anchoring it to the wall. Therefore, the EMT raceway is connected at the outlet box with a fitting, but not at the 4 square juction box in the ceiling. Conduit is secured in concrete, and junction box is secured to wall, so no movement possible between the two. The conductors are in the junction box and are protected entering the conduit by the plastic bushing, and all grounding connections at the outlet box, and juction box are attached providing a continuous ground for the system. The integrity of the electrical system wasn't compromised as far as I can see.
Question, reading 300.18 on raceway installations, I want to know what your opinion is about the exception which states, "Short sections of raceways used to contain conductors or cable assemblies for protection from physical damage shall not be required to be installed complete between outlet, junction, or splicing points."
Also 300.12 Exception No. 1
I 'm referencing this because of 358.30 which states, "EMT shall be installed as a complete system in accordance with 300.18..."
Does this cover the installation above? Any other comments welcome.
Thank You
Charlie O
Recently I was faced with a installation that involved a 3/4" EMT conduit connecting a outlet in a office to a juction box in the drop ceiling. The conduit is installed in a concrete filled non-moisture subjected block wall that separates offices inside a wherehouse. The conduit was cut too close to wall and right at the the pipes bending radius making it impossible to put a EMT connector on as to attach it to the 4 square junction box. Since the wall is block, and the EMT conduit is set in concrete, the only option I could see to do, minus cutting & jack hammering concrete and making a huge mess, was to install a hammer-on plastic bushing and put the 4 square box over the conduit, anchoring it to the wall. Therefore, the EMT raceway is connected at the outlet box with a fitting, but not at the 4 square juction box in the ceiling. Conduit is secured in concrete, and junction box is secured to wall, so no movement possible between the two. The conductors are in the junction box and are protected entering the conduit by the plastic bushing, and all grounding connections at the outlet box, and juction box are attached providing a continuous ground for the system. The integrity of the electrical system wasn't compromised as far as I can see.
Question, reading 300.18 on raceway installations, I want to know what your opinion is about the exception which states, "Short sections of raceways used to contain conductors or cable assemblies for protection from physical damage shall not be required to be installed complete between outlet, junction, or splicing points."
Also 300.12 Exception No. 1
I 'm referencing this because of 358.30 which states, "EMT shall be installed as a complete system in accordance with 300.18..."
Does this cover the installation above? Any other comments welcome.