ok cool that's what I thought but got confused when someone said it means a starter that protects a combination of motors, ie- 2 or more on one ckt
 
Look at the diagram in the beginning of Article 430, Figure 430.1

p2_pic2_en.gif


Everything from the "Supply" to the motor must be in each motor circuit. A "Motor Starter" in just the last two elements before the motor, the controller and the overload protection. A "Combination Motor Starter Starter" incorporates more of the elements above it, typically a fused disconnect (or non-fused if there is dedicated up-stream protection) or circuit breaker, along with the provisions to lock it out.

If you don't use a Combo, you have to have locking provisions on whatever your OCPD is for that circuit, and you must also have lockout provisions "within sight" of the motor (with lots of exceptions of course). Using a Combo starter cuts down on the interconnection of those separate elements.
 
ok cool that's what I thought but got confused when someone said it means a starter that protects a combination of motors, ie- 2 or more on one ckt
That would be called a "Grouped Motor Controller" or "Group-fused" control panel. The same circuit elements still need to be in each motor circuit, but you can get away with combining some of the more expensive parts.
 