KyleFowler
- Maryville, TN
- Electrician
Got a 0.5kva 480/240 to 240/120 single phase Hammond transformer to wire up and the diagram has this unexplained dot next to the windings of H1 and X1. On the Hammond website they actually do elaborate on the dot but for practical purposes their explanation isn't very helpful to me. Below is their explanation:
"The placement of these dots next to the ends of the primary and secondary windings informs us that the instantaneous voltage polarity seen across the primary winding will be the same across the secondary winding. In other words, the phase shift from primary to secondary will be zero degrees, which is important for some types of circuits. If the wiring to the dots is reversed on one side, the primary and secondary will be 180 degrees out of phase."
I want to know when I wire this transformer to step 480 volt down to 120 volt should the ungrounded conductor be X1 since it has the dot? That's my interpretation of the dot. I'm sure I really don't understand what Hammond is trying to tell me. Just trying to do my due diligence and not guess/test.
For a scope of work we are wiring a 0.5kva transformer to step down 480v to 120v to refeed a road sign that had it's original underground line cut underneath the building the sign is fed from. This apparently happened 20 years ago and no one cared until now. The 480 volt supply we are sourcing is from a pole light 50 feet away and the only power source available without cutting the parking lot or an underground bore etc. The road sign was converted from t12 HO to LED by a sign company recently with 120 volt drivers.