A set of design requirements includes the following text: "Outlets. The use of sealed or flush fittings is required; additional requirements as needed to create a 'spark-proof/resistant" outlet."

It relates to rooms in a parachute rigging facility, and specifically to the room in whick oxygen bottles are stored and the room where maintenance is conducted on oxygen masks (i.e., for high altitude drops).

A consulting engineering firm is saying that these rooms are Class 1, Division 1, and the quoted text appears to be their only basis. I think that that is nonsense.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
I'd say your correct Oxygen is a not a 'flammable gas', but it is fertilizer for fire and should be taken into consideration.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I'd say your correct Oxygen is a not a 'flammable gas', but it is fertilizer for fire and should be taken into consideration.
As in the Apollo 1 cabin fire in 1967 that killed Ed White, Gus Grissom, and Roger Chaffee.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
As a result of that fire, they stopped using 100% oxygen for breathing air and they did everything possible to remove combustible materials from the spacecraft.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
As a result of that fire, they stopped using 100% oxygen for breathing air and they did everything possible to remove combustible materials from the spacecraft.
Yes, but I am pretty sure that EVA suit breathing is still 100% O2 at low pressure, so going EVA requires a period of time breathing pure O2 ahead of time to avoid decompression sickness due to N2 in the blood.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
It definitely isn’t Class I; that is, the “fuel” isn’t a flammable gas, vapor, or liquid. [Section 500.5(B)] Even if it were, their description of an “outlet” wouldn’t necessarily meet the requirement of Section 501.145 if they just meant “receptacles” or more generally Section 501.10(A)(4).
.
 