Majority of raceways require support within first three feet of a termination of the raceway, most of the flexible conduits however do require first support within one foot.
There also is exceptions that allow for more then three feet, as well as more then the 12 inches for flexible conduits.
Many of us in the past figured because of how this is worded that a 3 foot length of raceway between two boxes was considered supported by those boxes, but then in 2011 they thought this three foot length needed a support no more then 18" from either end. I think they have changed that in 2014 but still is different then it was before 2011. But I still remember sitting in a CEU class with an inspector as the instructor and us discussing this some and coming to a reality conclusion that if you had a three foot length of 4 inch RMC between two cabinets - that strap the NEC thought we needed in that short length would be supported by the RMC much more so then the strap would have ever supported the RMC in such a situation.:roll: