hi, all.
the following was told to me by an engineer that desigens these devices. he asked for me not to use his name. if any of this seems to be misinformation i would appreciate comments.
i do industrial work so i am not involved with these. i questioned their use in my existing home. bottom line: i was told "since your(my) entire home is wired in emt and you have a qo load center with redundant ground, you have little use for afci's".
the reasons given were:
1) these devices are most effective at opening on a line to ground arc. with other types of arcs they become much less efective.
2) they provide very little protection beyond the recptacle. (which was what they were originally marketed for.) they do not provide much protection beyond ordinary breakers from a intermittent connection between line and netural or an intermittent arc in line only beyond the outlet (bad lamp cord). as far as a constricted cord causing too much resistence, ordinary breakers handle this just as well as afci's (they trip mainly on heat not overcurrent). although, quite a bit of heat has to be generated to trip either type of breaker. still, ignition of surrounding materials from heat is fairly rare.
3) the most likely scenario of a zip cord to cause ignition, "dead short", will instantly trip a ordinary breaker.
4) as far as a intermittant arc in a zip cord or a glowing connection at a nut is concerned, sparks are more likely to be a source of ignition than heat. these devices will trip on the later condition before heat becomes an issue, but not before sparks have been produced, if indeed they would be produced.
comments appreciated,
ron g.
the following was told to me by an engineer that desigens these devices. he asked for me not to use his name. if any of this seems to be misinformation i would appreciate comments.
i do industrial work so i am not involved with these. i questioned their use in my existing home. bottom line: i was told "since your(my) entire home is wired in emt and you have a qo load center with redundant ground, you have little use for afci's".
the reasons given were:
1) these devices are most effective at opening on a line to ground arc. with other types of arcs they become much less efective.
2) they provide very little protection beyond the recptacle. (which was what they were originally marketed for.) they do not provide much protection beyond ordinary breakers from a intermittent connection between line and netural or an intermittent arc in line only beyond the outlet (bad lamp cord). as far as a constricted cord causing too much resistence, ordinary breakers handle this just as well as afci's (they trip mainly on heat not overcurrent). although, quite a bit of heat has to be generated to trip either type of breaker. still, ignition of surrounding materials from heat is fairly rare.
3) the most likely scenario of a zip cord to cause ignition, "dead short", will instantly trip a ordinary breaker.
4) as far as a intermittant arc in a zip cord or a glowing connection at a nut is concerned, sparks are more likely to be a source of ignition than heat. these devices will trip on the later condition before heat becomes an issue, but not before sparks have been produced, if indeed they would be produced.
comments appreciated,
ron g.