So a 400 amp CB is rated to handle a 400 amp load calculation. Is it correct that the main breaker is called a 320 /400 /cb because it happens to be a 320 class designation. It does not refer to 320 AMPS. It could have been, for example, a 789 designation? (789/400 cb)
I understand that a continuous load on a 400 amp cb is limited to 320 amps, but isn't that taken care of in the load calculation by multiplying the LCL by 125% So if you have a calculated load of , say 384 amps, that includes continuous and non continuous loads, so a 400 amp CB is the proper size.
Also, what does it mean to have a CB rated for use at 100% of its rating?
I understand that a continuous load on a 400 amp cb is limited to 320 amps, but isn't that taken care of in the load calculation by multiplying the LCL by 125% So if you have a calculated load of , say 384 amps, that includes continuous and non continuous loads, so a 400 amp CB is the proper size.
Also, what does it mean to have a CB rated for use at 100% of its rating?