Re: What is a plenum space and what isn't?
But these sections also require compliance with 300.22. 300.22(B) does not allow these wiring methods to be installed.
EDIT: I see your point on 800.51, to an extent. I think all this section is saying is that in order for a cable to have a "P" at the end of it, it must be listed as plenum rated. I don't believe this in and of itself permits its use in a duct or plenum, however.
800.53 also requires compliance with 300.22. Because these cables are not permitted by 300.22(B), they are not allowed in a duct or plenum, even if plenum rated. They are, however, permitted in "other spaces".