Now, again, I am a newbie to the codes and trying to learn from those more experienced than I, but, correct me please:
If you have a meter on a pole, just a meter, mind you, and no disconnect into an underground conduit system for a normal home, or even most businesses, there are no fuses to regulate anything until you get to the main panel, where your service disconnect is. This is allowed to be derated, etc and so forth.
There are arguments that a firemans disconnect may be needed, but nothing concrete in most places at this time.
Above there was an argument that if a simple disconnect is used, non-fused, that this would not affect the service rating of the underground feed. This is similar to what has been used forever in Rural Farms and in many apartment complexes, where a pole mounted disconnect that is accessible only by fire poles and utility poles can reach it to disconnect the services at the top of the pole.
Why then would they require it to be fused? Because it is 600 amps rather than 400 or 200 or 100 amps? Just trying to understand not start more fuss... Because I really cannot see the difference here. Personally, would prefer to see a definition in the code to keep it as service until it hits main disconnect at panel, and keep any firefighter or other service related disconnects as service only but having trouble seeing why there is such a difference, or, is it that we are going to be seeing a future shift from three wire service entrance to a four wire service entrance with no derating and they are trying to do it step by step?
A means of disconnect must be provided at or near the closest point of entry to a structure.
Service Conductors are very limited to the length they can travel inside a structure once they get to the structure they are servicing.
Thus you generally see a Meter/Main or Fused Disconnect, Enclosed Circuit Breaker outside by a meter mounted on a house. or a Main Breaker in the panel directly behind the meter.
This, most times serves the purpose of both a disconnect and a means of overcurrent protection.
That 1st means of overcurrent protection is the determining point as to where the service conductors end and where a feeder begins.
If no overcurrent protection exists in the disconnect then the conductors passing through that disconnect from the utility are still Service Conductors.
If there is overcurrent protection in the disconnect, such as fuses, or if the Disconnect happens to be an Enclosed Circuit Breaker then the conductors on the line side of that disconnect are Service Conductors and the conductors on the load side of the overcurrent protections device are considered a feeder.
The rules of installation are different for Service Conductors versus Feeder Conductors.
A Service Rated disconnect has a Neutral terminal in it and a means to bond the neutral to the Grounding Electrode Conductor inside the disconnect.
Once that bond is made, the Grounded Conductor and the Equipment Grounding conductor must be kept separated from that point on. Thus a 4 wire feeder would be required.
The fuses, If installed out at the pole in a fused disconnect, are not there to "de rate" the service, they are there to protect the feeder conductors to the structure because an overcurrent protection device was installed making it such.
The decision to place the Overcurrent protection device remote from the structure is what brought the 4 wire feeder into affect.
The NEC is not trying to shift services from 3 wire to 4 wire at all.
The placement of the first means of overcurrent protection and where the first bond from the Grounded Conductor to the Grounding Electrode Conductor on the Customers side is what determines what type of installation you will end up with.
This is just a very non technical overview as if we were sitting on the tailgate trying to hammer this out.
JAP>