marmathsen
Senior Member
- Location
- Seattle, Washington ...ish
- Occupation
- Electrical Contractor
I just get called out for not having a lighting outlet in the closet under the stairs of a split entry home. The inspector quoted 2023 NEC 210.70 (C). I've always interrupted that to mean like a crawl space and I've never been called out for a closet. If you take that interpretation to the extreme then any space below the top floor of a house including every closet must have a lighting outlet.
How do you all interpret that requirement?
"2023 NEC
210.70 (C) All Occupancies.
For attics and underfloor spaces, utility rooms, and basements, at least one lighting outlet containing a switch or controlled by a wall switch or listed wall-mounted control device shall be installed where these spaces are used for storage or contain equipment requiring servicing. A point of control shall be at each entry that permits access to the attic and underfloor space, utility room, or basement. Where a lighting outlet is installed for equipment requiring service, the lighting outlet shall be installed at or near the equipment."
Rob G - Seattle
[Edited for typos]
How do you all interpret that requirement?
"2023 NEC
210.70 (C) All Occupancies.
For attics and underfloor spaces, utility rooms, and basements, at least one lighting outlet containing a switch or controlled by a wall switch or listed wall-mounted control device shall be installed where these spaces are used for storage or contain equipment requiring servicing. A point of control shall be at each entry that permits access to the attic and underfloor space, utility room, or basement. Where a lighting outlet is installed for equipment requiring service, the lighting outlet shall be installed at or near the equipment."
Rob G - Seattle
[Edited for typos]