jason sleeth
Member
- Location
- Illinois
A local Municipality has added an amendment to 720.11 as follows:
720.11 Mechanical Execution of Work. Circuits operating at less than 50 volts
shall be installed in a neat and workmanlike manner. Cables shall be supported
by the building structure in such a manner that the cable will not be damaged by
normal building use. ***All low voltage-type wiring systems shall be installed in
an approved raceway system acceptable to the Building Official. Non-metallic
raceway systems allowed for residential use only. Commercial concealed low
voltage-type wiring systems to be installed in metallic raceways***
Their intent was to require TV and phone to be run in conduit. The are incorrectly citing the code and should be referring to Section 8 Articles like 800 and 820 instead of chapter 7 articles.
720.4 states that the min conductor size is #12 etc. obviously not intended for tv and phone applications.
Can someone give me examples of what this section is referring to? Lighting controls under
50 volts like a mark 7 ballast or is it something entirely different?
720.11 Mechanical Execution of Work. Circuits operating at less than 50 volts
shall be installed in a neat and workmanlike manner. Cables shall be supported
by the building structure in such a manner that the cable will not be damaged by
normal building use. ***All low voltage-type wiring systems shall be installed in
an approved raceway system acceptable to the Building Official. Non-metallic
raceway systems allowed for residential use only. Commercial concealed low
voltage-type wiring systems to be installed in metallic raceways***
Their intent was to require TV and phone to be run in conduit. The are incorrectly citing the code and should be referring to Section 8 Articles like 800 and 820 instead of chapter 7 articles.
720.4 states that the min conductor size is #12 etc. obviously not intended for tv and phone applications.
Can someone give me examples of what this section is referring to? Lighting controls under
50 volts like a mark 7 ballast or is it something entirely different?