What is considered a service panel?
kjroller
Dawson Mn
Master electrician
Is a panel supplied by a separately derived system a Sub Panel or a Service Panel? I believe it is considered a sub panel but I am not sure.
By definition a Panel connected to a separately derived system is not a Service Panel.
Separately Derived System. An electrical power supply output, other than a service, having no direct connection(s) to circuit conductors of any other electrical source other than those established by grounding and bonding connections.
Service. The conductors and equipment connecting the serving utility to the wiring system of the premises served.
What if it's a utility transformer?
Since the definition of SDS excludes services, whether the secondary of a transformer is an SDS or not depends on the location of the service point. You could have identical electrical configurations where the service point is on the secondary side of the (utility-owned) transformer, and you have a service; or the service point is on the primary side of the (customer-owned) transformer, and the transformer secondary is an SDS.
Cheers, Wayne
Do you people call a panel with the main disconnect for an SDS a 'subpanel'?
I mean, 'subpanel' is not a code term, so it means whatever people use it to mean. I think it clearly is appropriate for a panel that isn't either service equipment or the main disco for a separately derived system. I think it definitely does not mean a service panel. If I wanted to be super clear about things, I'd also avoid using 'subpanel' for a panel that contained the first disconnecting means for an SDS.