Can anybody tell me the use of De-rating in electrical equipment and cables?
:?
:?
I'll just add that the derating of conductor ampacity is for the preservation of the insulation, not for the wires themselves.
Transformers also have to be derated for altitude.
You got me on this one (I'm a flatlander) what is the reasoning? Does it have anything to do with atmospheric pressure at higher elevations in regards to heat dissipation?
Pete
Does it have anything to do with atmospheric pressure at higher elevations in regards to heat dissipation?
I would say so too. The KVA rating of any component is based on its ability to reject heat to its surroundings. At higher altitudes, there is less air, and that makes it harder for a transformer to reject heat to the surrounding air.
Yes - heat dissipation. Mostly due to 'thinner air'. It doesn't kick in untill about 3000', and doesn't really matter much untill you get up to about 8000'. In the Denver area, we don't worry about it too much, but the mechanical engineers who spec the chillers & cooling towers always add the altitude to their requirements. I believe diesel generators also have an altitude adjustment.
db
I guess this is something the NEC looks at as a design consideration because I cannot recall anything in the NEC that even mentions elevations and derating for transformers or other equipment for that matter.
The NEC tells us to use equipment within it's ratings. The manufacturers determine the ratings.
I will have to look closer at the manufacturers instructions on transformer ratings...
I just don't recall ever seeing a requirement
They come with instructions?:jawdrop: