Thanks Jim…important point to remember, if I can.Yes. Even fused switches are tested with conductors so a 20A 100kAIC current limiting fuse would also protect #12 conductors.
Thanks Jim…important point to remember, if I can.Yes. Even fused switches are tested with conductors so a 20A 100kAIC current limiting fuse would also protect #12 conductors.
To add a little to this, if you have 100kA available how often do you have (or desire to have) 15 and 20 amp circuits connected to the equipment that has that much available? Often that is main distribution type equipment and only supplies feeders or if there is branch circuits they are some large capacity load. Usually your general use branch circuits are on some some feeder or even have a transformer in the path and the fault current at the origin of those branch circuits is likely below 10kA or at least has series rated components involved. At very least a 22-25 kA main breaker in that branch panel that is series rated for use with the 10kA branch breakers, which that combination will be covered even by most commonly used "load centers" you find in residential installs.However, you will have to find some way to limit the fault current on the line side of the 20 amp breaker that feeds these loads. Unlikely you will find one suitable for use with that high AIC.
Loose with the language is not serving you here. It is NOT about the motor, it is about the EQUIPMENT ahead of it. All electrical devices that control the flow of POWER (as opposed to control circuits) must be capable of surviving a short circuit event without entering into a “RUDE” condition (Rapid Unplanned Disassembly Event). That applies to breakers, disconnect switches, fuses and fuse holders, terminals, contactors, overload relays, solid state power devices, EVERYTHING in the power circuit, EXCEPT the motor or load device (heater) itself. Fuses and circuit breakers already have that baked into their “interrupt ratings), commonly shown as “AIC”, and fuse holders generally are rated for the fuses they can hold. But the rest of it must be tested and listed with the breakers or fuses based on the “let-through” energy they allow before clearing the fault.So all motors [technically motor controllers, but I'm going to be loose with my language and say "motors"], all motors everywhere, always, should have their available fault current calculated and compared against the controller's SCCR?
if you get a 5kA SCCR label on a piece of commercial or industrial equipment, it can be next to impossible to connect it.