What is the 2RID equation?

Status
Not open for further replies.

97catintenn

Senior Member
Location
Columbia, TN
Is it?

(2RID)/cmil?

Does R=resistance from Chp. 9 Table 8?
I=amps
D=does D equal distance one way?

and just clarify that I do divide by cmil at the end
 

Howard Burger

Senior Member
Sounds like R is sub. for K

Sounds like R is sub. for K

Bottom line: I don't know. But this sure sounds like the top half of the single-phase formula for voltage drop where the R is in place of K. K for these formulas is derived from table 8 of the NEC: for K multiply the area of a wire in circular mills by the resistance in ohms per 1000 feet as found in Table 8. You're pretty safe remembering K for Cu is 12.9 and Al is 21.2 (or 13 and 21 for simplicity), and yes, the bottom half of the formula is CM.
 

97catintenn

Senior Member
Location
Columbia, TN
It's a short formula to help you remember the calculation. The saying goes, "To Rid yourself of voltage drop" which then you would write 2RID

I just wanted to check on the exact numbers/varibles
 

Smart $

Esteemed Member
Location
Ohio
Is it?

(2RID)/cmil?

Does R=resistance from Chp. 9 Table 8?
I=amps
D=does D equal distance one way?

and just clarify that I do divide by cmil at the end
Close. You can use CH9-T8, but because you are likely running AC circuits, why not use CH9-T9?

R=resistance/1000ft from table
I=amps
D=one-way distance

...and the formula is Vd=2RID/1000 for single-phase. Replace 2 with 1.732 for 3? circuits.

You can also restructure the formula to backsolve for maximum R, then compare to the table value...

R=1000(V?%)?(2ID)

where "V" is the nominal voltage and "%" is the allowable voltage drop in per cent.

After solving for R, look in the table for the conductor, and its application if using T9, having a lesser R (or Z) value than your Vd-calculated R.
 

97catintenn

Senior Member
Location
Columbia, TN
Great! Thanks for posting.

I have 37kva 230v ciruit wtih 1/0 copper and a 450' run (one way) in PVC.

So, then I would calculate the amps 37va/230v= 160.86amps R from Chp 9 Table 9 0.39ohm (don't forget that you have divide 0.39/1000ft!)

Vd=(2RID)/1000
Vd=(2*.00039ohms*160.86amps*450')/1000

So, my voltage drop comes to 0.056volts.

That doesn't sound right. I'm double checking my answer by taking the 0.39ohm/1000ft*450'*160.86amps and I get 28.23v

Am I totally lost?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Great! Thanks for posting.

I have 37kva 230v ciruit wtih 1/0 copper and a 450' run (one way) in PVC.

So, then I would calculate the amps 37va/230v= 160.86amps R from Chp 9 Table 9 0.39ohm (don't forget that you have divide 0.39/1000ft!)

Vd=(2RID)/1000
Vd=(2*.00039ohms*160.86amps*450')/1000

So, my voltage drop comes to 0.056volts.

That doesn't sound right. I'm double checking my answer by taking the 0.39ohm/1000ft*450'*160.86amps and I get 28.23v

Am I totally lost?

The ohms/1000ft from table 9 is 0.12, not 0.39.

And you divided by 1000 twice. Using 0.39 would give you a 56 Volt drop, not a 0.056 Volt drop.
 
Last edited:

97catintenn

Senior Member
Location
Columbia, TN
Got it. I was confused about it because I saw one reference Vd=2RID and then later saw it as Vd=2RID/1000

So, now it makes sense why guys write it both ways. And you're right 0.39ohm is per 1000 meters...:dunce:
 