I'm using NEC 2011.
I'm attempting to determine the ampacity of a MLO 3-phase panel (commercial). It is being fed by 1/0 CU THHN/THWN. The 4" feeder conduit goes underground to an electrical room several stores away. Since it goes underground I'm thinking I have to use the THWN at 75 deg which gives 150 amps. Not sure If I'm supposed to derate since there is 3 hots and a neutral in there (more than 3 CCC).
I'm attempting to determine the ampacity of a MLO 3-phase panel (commercial). It is being fed by 1/0 CU THHN/THWN. The 4" feeder conduit goes underground to an electrical room several stores away. Since it goes underground I'm thinking I have to use the THWN at 75 deg which gives 150 amps. Not sure If I'm supposed to derate since there is 3 hots and a neutral in there (more than 3 CCC).