What is the ampacity of this panel?

Status
Not open for further replies.

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
I'm using NEC 2011.

I'm attempting to determine the ampacity of a MLO 3-phase panel (commercial). It is being fed by 1/0 CU THHN/THWN. The 4" feeder conduit goes underground to an electrical room several stores away. Since it goes underground I'm thinking I have to use the THWN at 75 deg which gives 150 amps. Not sure If I'm supposed to derate since there is 3 hots and a neutral in there (more than 3 CCC).
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Is unlikely that you have 4 CCC'S for derating purposes unless more than 50% of the load is nonlinear. If there are no other adjustments required you should be at 150 amps.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
I wouldn't count on wire size to indicate panel size. What if the engineer bumped the wire up because "it's from several stores away" and it's actually on a 100 amp breaker?

I'd find the breaker feeding it.
 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
I wouldn't count on wire size to indicate panel size. What if the engineer bumped the wire up because "it's from several stores away" and it's actually on a 100 amp breaker?

I'd find the breaker feeding it.

That's the next step. The panel itself is rated at 225 amps. I haven't gotten access to the electrical room yet to see what size the main breaker is.
 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
Is unlikely that you have 4 CCC'S for derating purposes unless more than 50% of the load is nonlinear. If there are no other adjustments required you should be at 150 amps.

Thanks, there is just a few motor loads from freezer, refridge and the RTU. Which code section talks about derating at >50% non-linear? I'd like to read it.
 