What is the code on splicing in condulets?
Someone at work said you can only splice in T's but im pretty sure i read its aloud in any condulet.
Never heard the T's only rumor, but it is not ANY conduit body.
Here you go.
314.16(C)(2) With Splices, Taps, or Devices. Only those conduit
bodies that are durably and legibly marked by the manufacturer
with their volume shall be permitted to contain
splices, taps, or devices. The maximum number of conductors
shall be calculated in accordance with 314.16(B). Conduit
bodies shall be supported in a rigid and secure manner.
370-6(c) in the 1990 code said in part: "Conduit bodies having provisions for less than three conduit entries shall not contain splices, taps or devices unless they comply with the provisions of 370-6(b) and are supported in a rigid and secure manner". 6(b) required a cubic inch marking on the conduit body and that the total volume of the conductors not exceed the capacity marked on the fitting.
Not very realistic in line voltage applications. If you have small conductors in a large conduit body then maybe.
Why do you say that? Line voltage size conductors can easily be spliced in smaller size condulets.
Roger
And if you upsize your condulet with a couple reducer bushings, you can splice them even more easily. :D How about a 1 1/2" C on a 1" pipe, for instance? I always like that option, like Chris mentioned.
Roger
Right now I'm looking at a ?" PVC LB. Marked 4.6cu/in. So If I wanted to put a joint on three #14's I'm at 6 cubes. How does this work in the real world?
As imuse said, upsize the condulet say to a 3/4 and it works pretty well in the real world. Remember devices can even be installed in condulets so a splice certainly wouldn't be a problem.
Roger