The NEC does not come into play.What is the maximum distance a meter can be located from its CT blocks?
Say for a 800A 240/120 4W 3PH service if an example is needed.
Does the NEC come in to play here? of just the manufacturers specs?
Thanks is advance.
The NEC does not come into play.
The CT specifications will list the maximum burden (series resistance of wiring and internal resistance of meter itself) which is allowed and still deliver the rated accuracy. As long as the wiring impedance does not go too high, there is no limit to the length.
Thanks GoldDigger!
Is there any (new?) way to CT a service with a clamp on type CT and not have to re terminate the service? Say a 800 ~ 1000A 240/120 4W 3PH ?
There are split core CTs, but I do not know whether POCO would accept them for billing purposes. Incorrect installation, not necessarily easily seen, would result in a systematically low output current.
Any answers from utility folks?
The NEC does not come into play.
The CT specifications will list the maximum burden (series resistance of wiring and internal resistance of meter itself) which is allowed and still deliver the rated accuracy. As long as the wiring impedance does not go too high, there is no limit to the length.
What is the maximum distance a meter can be located from its CT blocks?
Say for a 800A 240/120 4W 3PH service if an example is needed.
Does the NEC come in to play here? of just the manufacturers specs?
Thanks is advance.
I don't believe there is an NEC issue. However, from what I remember POCO's in my area require not more than 1 (10') length of 1 1/4" rigid gal between the meter and the CT. Not sure what their reasoning is.