What is the meaning of "-2" in RHW-2, THW-2, etc?
tuscon Az
Engineer
Hi All,
I remember this question from the exam. The question asked what does the "-2" signify in these cables. Is it 90C, Wet/Dry or both? I just want to make sure... Sorry if this is asked many times before...
Thank you!
Hi All,
Thank you!
If the -2 is missing then you will see that dry is 90C and wet is often 75C
Here is an example
Common is THHN/THWN/THW-2 marked conductor.
without the -2 it is only rated 90C as a THHN conductor and 75C as a THWN conductor. THHN is not rated for wet locations so you must use the THWN rating for wet locations.
With the -2 rating you have a conductor that is 90C rated for both wet and dry.