WHAT IS THE MINIMUM DEAPTH OF RIDGID PVC WITH SUB FEED WHEN UNDER WALK TRAFFIC ONLY

Status
Not open for further replies.

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Here is a graph to compare different installation methods.
 

Attachments

  • Wlectrical Wiring - Under Driveway.jpg
    Wlectrical Wiring - Under Driveway.jpg
    323.7 KB · Views: 22

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Here is another graph with different scenarios.
 

Attachments

  • Electrical Wiring - Undergrounding.jpg
    Electrical Wiring - Undergrounding.jpg
    373.4 KB · Views: 12

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Here is a graph to compare different installation methods.

How does this help the op and it seems to be inaccurate.

Pvc under a driveway not encased in concrete must be 24" down while your chart shows 18". That may be true for one and two family dwelling but it doesn't say that or I am just blind
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
The posted charts are for commercial, residential and industrial applications not public works, like streets, highways.
 