Why would they offer 1/2 hp 1.5 SF instead of just selling it as 3/4 hp at 1.0SF?
Why would they offer 1/2 hp 1.5 SF instead of just selling it as 3/4 hp at 1.0SF?
I think that's the question. If it can continuously deliver 3/4 HP, why not just call it what it is?While horsepower is a unit like watts, the horsepower rating of a motor includes about things like temperature rise, break-away torque, stall torque, etc.
So a 1/2 hp motor with a 1.5 sf implies 1/2 hp overall characteristics but the ability to deliver 3/4 without overheating.
-Jon
I think that's the question. If it can continuously deliver 3/4 HP, why not just call it what it is?
I think that's the question. If it can continuously deliver 3/4 HP, why not just call it what it is?
The horsepower rating and service factor tells you none of these things.Again the 'horsepower' rating implies a bunch of other characteristics such as peak torque (breakdown torque), starting torque, etc.
If the motor has the starting characteristics of a 1/2 Hp motor, but is thermally capable of 3/4 Hp output, what would you call it?
IMHO it probably makes more sense to break out all of these factors, and separately state the starting torque, breakdown torque, thermally limited output, etc. But if you want to dumb it dowm to one number....
-Jon
This I know.For the record.. IEC does not utilize SF like IEEE
Again the 'horsepower' rating implies a bunch of other characteristics such as peak torque (breakdown torque), starting torque, etc.
If the motor has the starting characteristics of a 1/2 Hp motor, but is thermally capable of 3/4 Hp output, what would you call it?
IMHO it probably makes more sense to break out all of these factors, and separately state the starting torque, breakdown torque, thermally limited output, etc. But if you want to dumb it dowm to one number....
-Jon
Are they even stated on the nameplate?Bingo. I'm not going to bother to look it up, but the official NEMA definition of motor "service factor" states something to the effect that if you use the SF, you can expect that the performance specs will NOT be as stated on the nameplate,
14.37.1 General
A general-purpose alternating-current motor or any alternating-current motor having a service factor
in accordance with 12.52 is suitable for continuous operation at rated load under the usual service
conditions given in 14.2. When the voltage and frequency are maintained at the value specified on the
nameplate, the motor may be overloaded up to the horsepower obtained by multiplying the rated
horsepower by the service factor shown on the nameplate.
When the motor is operated at any service factor greater than 1, it may have efficiency, power factor,
and speed different from those at rated load, but the locked-rotor torque and current and breakdown
torque will remain unchanged.
A motor operating continuously at any service factor grater than 1 will have a reduced life expectancy
compared to operating at its rated nameplate horsepower. Insulation life and bearing life are reduced by
the service factor load.