Table 310.15 and the older one 310.16 list number 14 for 20 amps, 12 for 25 and 10 for 35, but why the blanket rating of 15, 20 and 30 amps?
What got me wondering was another code violation handy man special:roll: HO window AC breaker kept tripping and someone had replaced the 15 with a 20. The amp draw was around 19 to 20 amps with a clamp on meter but contrary to what some say the wire was barely warm. No molten or burning insulation. Heck I have even seen 14 on 30amp fuses get hot, but not burn up let alone get over 140 degrees.
What is the theory behind the restriction?
What got me wondering was another code violation handy man special:roll: HO window AC breaker kept tripping and someone had replaced the 15 with a 20. The amp draw was around 19 to 20 amps with a clamp on meter but contrary to what some say the wire was barely warm. No molten or burning insulation. Heck I have even seen 14 on 30amp fuses get hot, but not burn up let alone get over 140 degrees.
What is the theory behind the restriction?