First: what resource or software do you guys use to calculate SCCR of a panel or circuit??
Second: Can anyone help identify what the SCCR would be for this circuit. i am trying to achieve a 65kVA.
View attachment 23339
Thanks for any help,
Sam
Let me just state that we can help you but you cannot use the company name for advertising. That is not allowed.
Your question is a little non-specific. The way it works is everything in a power circuit has to have a SCCR. The smallest rating is what determines the overall rating, although some items that have a relatively low SCCR by themselves can have a much higher rating when combined with some other component.
Its also not real clear to me what you mean by a panel. If you mean a panelboard than the manufacturer would specify what it is based on the components you selected.
If the panel is a control panel, than UL508a would be used to evaluate its SCCR.
Hey Dennis thanks for the reply and are you referring to ******
if so i didn't know it wasn't allowed just signed up to these forums.
Hey petersonra,
i have two panels, my panel has a CB rated at 65kA with a transformer 15kVA which is feeding a second panel (third party vendor) rated at 5kA.
So, do i have to have a 65kA CB with a 65kA transformer and the sub panel rated at 65kA ?
That is neither an SCCR nor an SCCA. That is an AIC - an acronym that has several possible meanings. I prefer "Amps Interrupting Capability," but other choices are available. It refers to the amount of current that can pass through the breaker's metal contacts without heating them up so severely that they melt together, forever thereafter preventing the breaker from opening.. . . my panel has a CB rated at 65kA. . . .
I believe you meant that a new SCCA is established. See my post #8 above.After the Transformer a new SCCR is established.
That is neither an SCCR nor an SCCA. That is an AIC - an acronym that has several possible meanings. I prefer "Amps Interrupting Capability," but other choices are available. It refers to the amount of current that can pass through the breaker's metal contacts without heating them up so severely that they melt together, forever thereafter preventing the breaker from opening.
I believe you meant that a new SCCA is established. See my post #8 above.
okay.
i am confused :? all i know is, if i am building a panel who's name plate should read SCCR: 65kA.
i need to have all my CB's (feeder circuit) rated at 65kA
and all other component should also be rated at 65kA if they are part of the feeder circuit.
some are excluded per S.B 4.2.1 (i.e filters reactors ..etc)
Also, as i understand if i have transformer which doesn't have SCCR and is excluded per UL S.B 4.2.1
anything after a transformer should not affect my the SCCR rating of the panel.
do i make sense or do i have this completely wrong ??
i have two panels, my panel has a CB rated at 65kA with a transformer 15kVA which is feeding a second panel (third party vendor) rated at 5kA.
So, do i have to have a 65kA CB with a 65kA transformer and the sub panel rated at 65kA ?