The technical term I use is, "lost one phase". "3-phase system" is usually clear from the context.What is the techincal for lost of one phase of a 3-phase system? ...
When a piece of 3 phase equipment (such as a motor) is running with one phase out, what is the name for that situation???
It is as far as I know.I have always referred that situation as "single phasing", but I don't know if that is the technical term for the situation.
Chris
When you lose one transformer of a 3 phase delta bank, you can continue to provide power at about 60%. When you lose a phase you can't supply power to 3 phase equipment.He may be referring to an "open delta" ? When a delta connected system loses a phase to a building or other structure the load can continue to be served but at only 60%
"Phase loss" as in phase loss detection and protection in monitoring 3? fire suppression equipment.What is the techincal for lost of one phase of a 3-phase system? From time-to-time a phase of the power pole is loss and 1/3 of a building power is lost. When a piece of 3 phase equipment (such as a motor) is running with one phase out, what is the name for that situation???
What is the techincal for lost of one phase of a 3-phase system? From time-to-time a phase of the power pole is loss and 1/3 of a building power is lost. When a piece of 3 phase equipment (such as a motor) is running with one phase out, what is the name for that situation???
The single-phasing condition can occur on the secondary or primary side of the transformer. It makes a difference as to how the motor is connected and if the source transformer is wye/delta (or delta/wye).It might be that one 'phase leg', as I like to call the individual (usually) ungrounded conductors, has become disconnected after the transformers, or that an entire phase winding (between two {or more} legs) is no longer producing a voltage.