What is this?

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This is an out of the box 1Ø, 480 volt, 200 amp fused disconnect. Any idea what the #1/0 jumper is for?

IMG_20160818_094058.jpg
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I have seen that where the disconnect is used for DC. You need more contact interruption distance for DC than you do for AC and one way to get that is to series two contacts. I have seen instructions that called for that so you could use an AC disconnect for DC.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
That makes sense but why a #1/0 jumper for 200 amps, wouldn't the terminals be rated for only 75° C?

Also for AC would you remove the jumper?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
That makes sense but why a #1/0 jumper for 200 amps, wouldn't the terminals be rated for only 75° C?

Also for AC would you remove the jumper?
It is a factory installed jumper so the NEC ampacities do not apply. Even if the NEC did apply I think you could use Table 310.15(B)(17).
Being that is a factory jumper, that disconnect may not be listed for AC use. If it is listed, I see no reason to remove the jumper.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It is a factory installed jumper so the NEC ampacities do not apply. Even if the NEC did apply I think you could use Table 310.15(B)(17).
Being that is a factory jumper, that disconnect may not be listed for AC use. If it is listed, I see no reason to remove the jumper.


You never cease to amaze me. :thumbsup:
 

iwire

Moderator
Staff member
Location
Massachusetts
Sometimes the instructions call for doing this in the field when dealing with DC. I have run into it with solar.

And yeah, Don is pretty amazing. :cool:
 

kwired

Electron manager
Location
NE Nebraska
It is a factory installed jumper so the NEC ampacities do not apply. Even if the NEC did apply I think you could use Table 310.15(B)(17).
Being that is a factory jumper, that disconnect may not be listed for AC use. If it is listed, I see no reason to remove the jumper.
I see that kind of thing in pump panels, panelboards, etc. all the time. Factory installed (or even factory supplied but field installed) leads between components that are otherwise smaller then what you would have to use if assembling same components that are not part of a listed assembly.

In pump panels I often see as little as 2 AWG conductor between the disconnect and the motor starter yet the minimum NEC required conductor for the motor being supplied is as much as 2/0. Also seen many short pre formed conductor links as part of a main breaker kit to install in a panelboard that are not the same size as I would have to install if NEC applied to them.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I agree, does anyone have a document that shows this? I've been poking around but am coming up empty and I know that people will be asking. :)

Are you asking for a document showing that Don is amazing or a document showing that what Don said is true?
If the former, I think his Mom wrote one up!:D
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The following is from a Eaton document for their solar DC disconnects.
Switching devices primarily designed for DC service require design features to increase the total arcing voltage. This can be achieved by designing larger single air gaps and multiple gaps in series, or by using magnetic fields to force arc movement.
You watch a demo of a knife switch open a 2600 watt load at 220 AC and at 220 DC in this youtube video.
https://www.youtube.com/watch?v=Zez2r1RPpWY
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I bought some 1-phase heavy duty Eaton disconnects awhile back that came like this. Was also curious ..... Now I know


Sent from my iPhone using Tapatalk
 

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
Why does 220VDC arc like that? Is that really 220VDC? Looks like a LOT more.

its 220ac(rms) and its 220dc(rms). no filtering thus a bunch of dc humps at 120hz. the zero crossing of ac is a good quenching process.
if its US resi then its really 240v
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I want a document that verifies Don's mom stated that what he said is truly amazing. Preferably notarized and such if possible.:p

Well, there is this


Roger
 

Attachments

  • newspaper.jpg
    newspaper.jpg
    35 KB · Views: 7

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Yes it's listed AC or DC.

From the label, it looks like it is listed for DC or _single phase_ AC. I don't see it listed for 3 phase use.

IMHO the jumper has to stay for any of the uses listed on the label.

It wouldn't surprise me if the assembly sans jumper with a different label is listed for 3 phase use. I also would not be surprised if the 'matching' 3 phase device had a lower voltage rating or different short circuit ratings.

-Jon
 

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
DC has no zero volt crossing like AC to "assist" with extinguishing the arc.

this particular DC does have a zero "crossing" @ 120Hz :thumbsup:

that same video using full bridge rectifier at say 30Hz or 200Hz (AC) will show way different results.

a 240 battery, even more different results.
 