All of your calculations are hidden in your spreadsheet...which means no one can really comment on what's wrong with it. Is the result not what you are expecting? As kingpb asked, what do you think is wrong?
To answer kingpb's question... In some municipalities, the building department and plan reviewers require you to show voltage drop calculation results. Especially for 120V motors/actuators. You can get to 3% pretty quickly running #12's that are drawing 2-3 amps.
I don't tend to show them for the feed between transformers and load panels since they are typically very close to one another and runs are ~5-10 ft and it seems the plan reviewers we work with are okay with that. However, I would definitely show it for a 113A, 90 ft run. Although the wire size is much larger than the load it appears. So V.D. should, in theory, not be an issue. It still should be documented so the engineer can demonstrate due diligence. Just my opinion.