I was involved in a recent complaint in a rural area where 6 volts was measured between the water well and the earth. I used an O-scope and saw a 60Hz sine wave. The voltage varied and many checks were made over time. The short story is I wound up at the POCO substation and measured 5 volts checking from the POCO pole ground wire to a screwdriver stuck in the ground. This pole check was ten feet from their fence. I was using a Fluke 345 so I saw the AC & DC content and could switch over to see the sine wave. All looked liked AC to me. I did get one measurement that was as high as 10 volts measuring from a bonded guy wire to the substation fence. Concerned that it was all make believe, I drug out my Sidekick analog telecom meter. The needle swung up to 10 volts AC.
I was thinking that this would be an easy sell, but I was wrong.
The POCO rep responded with this: "The voltage registered near the station would be expected (due to any imbalance and higher impedance of the earth), due to returning current through the pole grounds and neutral back to the sub. "
I do not agree. Please explain how this can be acceptable and what is a big number where someone should be concerned?
I was thinking that this would be an easy sell, but I was wrong.
The POCO rep responded with this: "The voltage registered near the station would be expected (due to any imbalance and higher impedance of the earth), due to returning current through the pole grounds and neutral back to the sub. "
I do not agree. Please explain how this can be acceptable and what is a big number where someone should be concerned?