In previous code cycles 705.31 specified that the length of supply side connected PV conductors between the point of interconnection and the OCPD shall be 10' or less unless cable limiters are present at the connection point, but 705.31 has been removed from the 2020 NEC. What is the governing code language now for supply side connected PV conductors?
ggunn
Austin, TX, USA
Never mind; I found it: 705.11