May I ask you a question what is the practical and scientific differance between single phase and 2 phases from 3 phase transformer?
 
Dear friends.
May I ask you a question what is the practical and scientific differance between single phase and 2 phases from 3 phase transformer?
Almost none from a practical use standpoint. In the case of 2-out-of-3 phases, the voltage reference would ONLY apply to a Line-to-Line voltage. When using the broader definition of "single phase", the term could also be inclusive of Line to Neutral voltage levels. But if you are looking at 240V from a single phase transformer, or 240V from 2-out-of-3 phases on a 240V Delta 3 phase transformer, the details are lost on the load, it will not make a difference.
 
But capacitive leakage and voltage from terminals to ground will be different, and that can affect the behavior of an appliance that contains the line to line load.
 
140710-2211 EDT

darekelec:

There may be a big difference depending upon what is the reason and basis for your question.

For example:

If you connect a TED 1000 energy monitor to a split-single phase source the power and energy measurements will be approximately correct. Connect to two phases of a 3-phase system and there can be a substantial error.

Connect a 10 ohm resistor line-to-line to the two different sources and the power dissipated will be different. Less on the 3-phase system because line-to-line is 208 and not 240.

On the center tapped single phase system the two voltages relative to the center tap are 180 deg out of phase. On the 3-phase Y system the phase shift of one line to Y-center is 120 deg out of phase with either of the other two lines to Y-center.

.
 