I have to feed a cord and plug connected compressor package (2 motors / 1ph 208V) with a package FLA of 18A (nameplate). The factory installed plug is rated for 20A.
Per 210-23 A (1) "utilization equipment shall not exceed 80% of the branch circuit rating",
Per 210-21 B (1) you need a 30A receptacle for a 30A circuit.
What size branch circuit and receptacle can I use without modifying the compressor.
Thanks in advance
Per 210-23 A (1) "utilization equipment shall not exceed 80% of the branch circuit rating",
Per 210-21 B (1) you need a 30A receptacle for a 30A circuit.
What size branch circuit and receptacle can I use without modifying the compressor.
Thanks in advance