where or who said this is a continuos load situation?brichter said:I'm confused. Whay would 80% have anything to dowith it. It is not a continuous load.
I'd be willing to bet that the 3/4 HP rating is inflated, and the actual label states a much lower amperage.augie47 said:are garbage dispoal motors rated differently ? 430.248 shows 3/4 hp at 13.8 amps. spells overloaded to me.
LarryFine said:I'd be willing to bet that the 3/4 HP rating is inflated, and the actual label states a much lower amperage.
Have a clamp-on ammeter handy?
brichter said:I'm confused. Whay would 80% have anything to dowith it. It is not a continuous load.
I checked out a kitchen aide disposal 3/4 hp and it was rated about 7 ampsaugie47 said:are garbage dispoal motors rated differently ? 430.248 shows 3/4 hp at 13.8 amps. spells overloaded to me.
m73214 said:A continuous load would require a circuit rated at 125% of the calculated load. The 80% is the maximum a circuit should be loaded under normal conditions.
hardworkingstiff said:Larry, aren't we required to use the NEC rating when we size the conductors for motors (in lieu of the nameplate)?
Can you clarify your response?l3city said::smile: check NEC 210.21(B)(2)
l3city said::smile: check NEC 210.21(B)(2)
Exception No. 3: For a listed motor-operated appliance that is marked with both motor horsepower and full-load current, the motor full-load current marked on the nameplate of the appliance shall be used instead of the horsepower rating on the appliance nameplate to determine the ampacity or rating of the disconnecting means, the branch-circuit conductors, the controller, the branch-circuit short-circuit and ground-fault protection, and any separate overload protection.
Dennis Alwon said:I don't believe this is true. You could load a 200 amp service to 195 amps if you wanted as long as it wasn't continuous.
.
I don't disagree with anything, but would like to add that series wound motors, with brushes, behave far differently from the "induction" motors listed in the table. I don't THINK the typical inrush exists at all.LarryFine said:I'd be willing to bet that the 3/4 HP rating is inflated, and the actual label states a much lower amperage.
Have a clamp-on ammeter handy?