I have a 120/240 100A lighting panel with (12) 20A 1P breakers. I need to wire the (12) circuits to a 12P lighting contactor and I am trying to figure out the easiest way to go about it.
I want to avoid an individual conduit run for each circuit. Initially I started with a single conduit run with (12) circuit conductors from the breakers, (1) neutral, and (1) EGC in a single conduit run. Issue I have here is that the 2AWG neutral is derated to 3/0AWG because of 12 CCCs in a single conduit. 3/0AWG is too large to adequately terminate at the panel and the lighting contactor. So rather than doing a single run, and an individual run for each circuit, I want to meet in the middle. I am looking to have 3 conduit runs, (4) circuit conductors in each. Now this is where I need some feedback. I'm fairly certain I need to run a neutral in every conduit per 300.3(B).
My questions is, since I will have to run (3) neutrals between the panel and the lighting contactor, does each neutral have to be sized for the ampacity of all circuits, or only the circuits it is run with (ie. 1/3, or 4 of the 12 circuits)? It'll make derating/running the neutrals a lot easier...
I want to avoid an individual conduit run for each circuit. Initially I started with a single conduit run with (12) circuit conductors from the breakers, (1) neutral, and (1) EGC in a single conduit run. Issue I have here is that the 2AWG neutral is derated to 3/0AWG because of 12 CCCs in a single conduit. 3/0AWG is too large to adequately terminate at the panel and the lighting contactor. So rather than doing a single run, and an individual run for each circuit, I want to meet in the middle. I am looking to have 3 conduit runs, (4) circuit conductors in each. Now this is where I need some feedback. I'm fairly certain I need to run a neutral in every conduit per 300.3(B).
My questions is, since I will have to run (3) neutrals between the panel and the lighting contactor, does each neutral have to be sized for the ampacity of all circuits, or only the circuits it is run with (ie. 1/3, or 4 of the 12 circuits)? It'll make derating/running the neutrals a lot easier...