fbhwt
Electrical Systems Inspector
- Location
- Spotsylvania,Virginia
- Occupation
- Electrical Systems Inspector
I am in dispute over the size equipment grounding conductor needed. Service is 1000a ,208v, 3ph
3 sets of 4-400mcm from 1000a service disconnect to 1000a transfer switch. I say it should be 2/0 copper or 4/0 alu according to 250.122, disconnect is fused at 1000a
3 sets of 4-400mcm from 1000a service disconnect to 1000a transfer switch. I say it should be 2/0 copper or 4/0 alu according to 250.122, disconnect is fused at 1000a