Ohm2
Member
- Location
- Washington
- Occupation
- Electrician
Ok this site has two triplex buildings. Both buildings have a ufer (rebar is 1/2in). Building 1 has the service ( 600a) and hits the ufer with a #4cu—then each unit has a #4cu to an accessible ufer. Building 1 serves the detached tri-plex ( building 2) with 1/0 1/0 2Al with a #6 EGC. Building 2 has access to the ufer ( rebar is 1/2 in) in each unit ( same as building 1). What size GEC shall be installed from the non-serviced rated panel to the ufer. Do we use T250.66 based on the largest ungrounded conductor or is it going to be a min number 4cu per 250.52(A)3. Or am I thinking too much