LA-Sean
Member
- Location
- Los Angeles
- Occupation
- General Contractor
My utility is giving me a single drop with a Single Phase 400AMP Conductor rated a 80%. So technically only 320AMPs. I need to upgrade my current configuration to a 400 AMP Disconnect with a Meter Module Configuration of 3 columns with 4 Stackable Meter Column, 3 Stackable Meter Column , and 3 Stackable Meter Column. So, a total of 10 Meter Spaces. 3 of which are spares for Future development. I currently have a total of 6 Apartment Units with individual meters, and 1 Common Area Meter.
My first Question: If I have 400 AMPs Disconnect what is the highest load, I can provide my Apartment Subpanels without a disruptions? What should be the Breaker Size at the Meter for the individual Apartments and what should be the Breaker Size of the corresponding Apartment Subpanel. I have received conflicting answers from electricians. Some say, I am only limited to a maximum of 60 AMP at the Meter and 60 AMP at the Subpanel. Others have said 80AMP outside and 125AMP at the Subpanel.
Here is some background: It so tough to get insurance for a small Multifamily building in California due to all the Disaster we have had here in the state Lately. This build has been in our family for decades. Our insurance company is requiring us to upgrade our electrical. We currently have the old Federal Pacific Panels. And we have never had any issues. There is 1 Utility Drop to the Building, 6 Apartment Units with individual Meters and Panel with 30 AMPS Each that runs to a subpanel on the interior of each unit. And there is 1 Panel for the common area which is also 30AMP mainly for exterior lights and garage door openers. I figured that if I am being forced upgrade the Electrical, I might as well get as much value out of it as I can. And since the government is forcing us to transition our Natural Gas Appliances to Electrical. I might as well do that at the same time.
When I started doing research on the electrical appliances. I found out that these appliances need a lot of Amperage. Electric Water Heater = 75 AMP with 2 double pole breakers of the 40AMP each, Electric Stove = 50 AMP Double Pole, Dryer = 35 AMP, Center HVAC 30AMP. After doing the Load calculation for all the connections. I found out that if I wanted to Electrify everything in the each of the units. I would probably need about 150 AMP Subpanel for each Unit.
I went to the Planner for the local Utility and asked the for my options. They said that I have overhead Service and the Maximum they can provide is 400AMP Conductor rated at 80%. So technically only 320AMPs. Their tariff only allows them to have 1 Drop per location for the same Voltage. I could have a One phase Drop and a three-phase drop but I don’t even know what do with a 3 Phase. And I don’t want to burden my tenants with additional cost of paying commercial rates with a 3-Phase. The 2nd option he offered was to go underground. But that would mean that I would need to pay and put this huge transformer on my property with 3-ft clearance all around and 7-ft in front of it. That is impossible because I don’t have the money or the space for that. Last option was to have put a larger transformer on the Pole and run the lines underground. And Utility Planner came to do a Site Survey. He saw the electric pole that is located at the far corner of my property but the Space around it is super limited, and he thinks that it cannot handle more then 1 riser. Thus, he concluded that I will only be limited to a 400AMP (320AMP Actual) connected overhead.
So here is my Second Question. Suppose that in the future my Utility is forced to take all the lines underground, or give me a second drops, or can give me 600AMP to 800AMP conductor. What should I do with my current upgrade where I am limited to 400AMPs, so I can set myself up to save money on a future upgrade. Here is what I was considering: (a) Purchase Meter Modules that rated for high Amperage like 150A or Higher per Meter but for now only put an 60A to 80A Breaker in it due to the limit of the 400A Disconnect (b) Run #2 or #1 Wire to the Subpanels that is rated for 150A but for now put only an 80A to 100A main Breaker in it. (c) Run all the homeruns to the Electrical Appliances from the Subpanel but for now leave them idle/not connect them to a breaker nor provide the outlet. So, I don’t have to destroy any drywall in the future.
Would this mean that all I would need to do for a Future Upgrade is to just upgrade the Disconnect to 600A or 800A. Change the Meter Breakers to 125A or 150A. And Change the Main Breaker on the Subpanels to 125A or 150A and connect all the idle wires to breakers and put in the outlets. Does this plan have any merit?
My first Question: If I have 400 AMPs Disconnect what is the highest load, I can provide my Apartment Subpanels without a disruptions? What should be the Breaker Size at the Meter for the individual Apartments and what should be the Breaker Size of the corresponding Apartment Subpanel. I have received conflicting answers from electricians. Some say, I am only limited to a maximum of 60 AMP at the Meter and 60 AMP at the Subpanel. Others have said 80AMP outside and 125AMP at the Subpanel.
Here is some background: It so tough to get insurance for a small Multifamily building in California due to all the Disaster we have had here in the state Lately. This build has been in our family for decades. Our insurance company is requiring us to upgrade our electrical. We currently have the old Federal Pacific Panels. And we have never had any issues. There is 1 Utility Drop to the Building, 6 Apartment Units with individual Meters and Panel with 30 AMPS Each that runs to a subpanel on the interior of each unit. And there is 1 Panel for the common area which is also 30AMP mainly for exterior lights and garage door openers. I figured that if I am being forced upgrade the Electrical, I might as well get as much value out of it as I can. And since the government is forcing us to transition our Natural Gas Appliances to Electrical. I might as well do that at the same time.
When I started doing research on the electrical appliances. I found out that these appliances need a lot of Amperage. Electric Water Heater = 75 AMP with 2 double pole breakers of the 40AMP each, Electric Stove = 50 AMP Double Pole, Dryer = 35 AMP, Center HVAC 30AMP. After doing the Load calculation for all the connections. I found out that if I wanted to Electrify everything in the each of the units. I would probably need about 150 AMP Subpanel for each Unit.
I went to the Planner for the local Utility and asked the for my options. They said that I have overhead Service and the Maximum they can provide is 400AMP Conductor rated at 80%. So technically only 320AMPs. Their tariff only allows them to have 1 Drop per location for the same Voltage. I could have a One phase Drop and a three-phase drop but I don’t even know what do with a 3 Phase. And I don’t want to burden my tenants with additional cost of paying commercial rates with a 3-Phase. The 2nd option he offered was to go underground. But that would mean that I would need to pay and put this huge transformer on my property with 3-ft clearance all around and 7-ft in front of it. That is impossible because I don’t have the money or the space for that. Last option was to have put a larger transformer on the Pole and run the lines underground. And Utility Planner came to do a Site Survey. He saw the electric pole that is located at the far corner of my property but the Space around it is super limited, and he thinks that it cannot handle more then 1 riser. Thus, he concluded that I will only be limited to a 400AMP (320AMP Actual) connected overhead.
So here is my Second Question. Suppose that in the future my Utility is forced to take all the lines underground, or give me a second drops, or can give me 600AMP to 800AMP conductor. What should I do with my current upgrade where I am limited to 400AMPs, so I can set myself up to save money on a future upgrade. Here is what I was considering: (a) Purchase Meter Modules that rated for high Amperage like 150A or Higher per Meter but for now only put an 60A to 80A Breaker in it due to the limit of the 400A Disconnect (b) Run #2 or #1 Wire to the Subpanels that is rated for 150A but for now put only an 80A to 100A main Breaker in it. (c) Run all the homeruns to the Electrical Appliances from the Subpanel but for now leave them idle/not connect them to a breaker nor provide the outlet. So, I don’t have to destroy any drywall in the future.
Would this mean that all I would need to do for a Future Upgrade is to just upgrade the Disconnect to 600A or 800A. Change the Meter Breakers to 125A or 150A. And Change the Main Breaker on the Subpanels to 125A or 150A and connect all the idle wires to breakers and put in the outlets. Does this plan have any merit?