what size of transformer ?

Status
Not open for further replies.

orly_566

New member
i need to install an additional transformer ( indoor type ) to our building .The load is 470 Amps , 1 phase , 220v / 110v , 60 hz. ,the primary source will come from another transformer ( 460v , 3 phase , 60 hz.) What size of transformer and protection do i need ? , can i use 3 phase transformer?
 

iwire

Moderator
Staff member
Location
Massachusetts
I have to say your requirements seem a bit odd.

Can you explain what your supplying?

You need 470 amps single phase @ 220/110 volts?

That appears to be 103 KW but without knowing more about the installation I would not count on it.

If you have both 220 and 110 volt loads I would be thinking a three phase transformer supplying a 3 phase panel so we can balance the load on the supply system.
 
Status
Not open for further replies.
Top