mxlplx00
- Watsonville, California
- Electrician
I have a job at an auto wrecking yard. There are 100 amp fuses from the main panel (240v single phase) run 100 feet to a small 100 amp 8 space panel. From there we have #4 - 3 wires in EMT (240V single phase) run 100 feet to a 12 space 100 amp main breaker.
The 1st Sub-panel has a 5 hp air compressor, a 50 amp welder, some car battery chargers and a 20 receptacle circuit. The 2nd panel has a couple of 20 amp circuits and a 50 amp welder.
So from what I have read I'm only allowed to use the 60 degree column (table 310.16) for anything under 100 amps but have also read somewhere that if it's in a raceway that I could use the 75 degree column (85A for #4) in which case I could go the next standard size to a 90 amp breaker in the first sub-panel to feed the second sub-panel. Is this actually the case?
It seems to me it would be preferable if I had #4 all the way and tap the 2 sub-panels.
Pleas point out what's wrong with my thinking here.
Thanks
Marc
Thanks
Marc