What size protection for an Electric Hot Water Heater at 45kW

Status
Not open for further replies.

BatmanisWatching1987

Senior Member
Location
NJ
Occupation
Jr. EE
The plumber told me he will be installing a 45kW (208V/3P) Electric Hot Water Heater.

Should I use a 150A or 175A Breaker?

(45kW/ √3) * 208) * 1.25= 156.13A
 
You need to see the specs for the heater. Some require multiple branch circuits while others do the required load sub division internally.
 
If this water heater is more than 120 gallons then you don't need 125% based on 422.13

That means 125 amps and the literature appears to support that.
 