what size uf cable

Status
Not open for further replies.
The length of cable does not affect its ampacity right? Does the NEC require that the length of the cable be taken into consideration as well?
 
The length of cable does not affect its ampacity right? Does the NEC require that the length of the cable be taken into consideration as well?
Length of cable will not effect of ampacity of the cable, 10 amps will still create same amount of heat in same sized conductor at any cross sectional point. Length will change circuit resistance and that normally 10 amp load will end up being less than 10 amps for resistive load anyway. Inductive loads very well may draw more amps if voltage is low at the load, causing even more voltage drop and more current to be drawn.
 
First question you have to ask yourself is how much voltage drop is acceptable for the application?
After determining that and the minimum size wire, the next question is whether running a higher voltage circuit with a step down transfomer at the load end would be more cost effective.
 
Note that UF cable may be problematic. If you upsize the ungrounded conductor, you need to upsize the grounding wire proporationately. If 10-2 was large enough, you'd be OK. But 8-2 and 6-2 still use a #10 ground which is too small. I think you're looking at 8-2 or 6-2 unless you can tolerate the voltage drop of a 10-2 cable. You may need to go the transformer route, even if just a 120-240 1 KVA transformer.

Can you change the load to 240V?
 
Note that UF cable may be problematic. If you upsize the ungrounded conductor, you need to upsize the grounding wire proportionately. If 10-2 was large enough, you'd be OK. But 8-2 and 6-2 still use a #10 ground which is too small. I think you're looking at 8-2 or 6-2 unless you can tolerate the voltage drop of a 10-2 cable. You may need to go the transformer route, even if just a 120-240 1 KVA transformer.

Can you change the load to 240V?
 