what size wire for a 10kw heater

Status
Not open for further replies.
10kw heater with a 60 amp breaker on board. I have been told 8 gauge but I know that 8 gauge does not handle 60 amps. but I can get away with the 60 because we can rate the OCPD at 125% which brings it up to around 52.7 amps the next highest breaker is 60 amps does this sound right. the reason I ask is I have the ac man telling me he will fail inspection for the wire but I have done this before and I have been told b y inspectors that this is okay does this sound right thanks Ryan
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
What is the voltage? Let me presume it is 240 volts, single phase. 10,000 watts divided by 240 is 41.6 amps. This is a "continuous load" so the wires must have an ampacity of 125% of 41.6 amps, which is 52 amps. I don't have my book handy, so I don't know if a #8 will suffice. I will say that you must have a wire with an ampacity of at least 52. You can use a 60 amp breaker on such a wire, since it is the next higher rated overcurrent device.

Welcome to the forum.
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
What type wiring method will be used, NM or conduit? If NM I would feel comfortable with #6 @ 55amp, on 60amp breaker. Table 310.16 60deg due to 334.80 Ampacity requirement.
 
Last edited:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I use #6 Cu NM for 10kw/240v, also. If it were 208v, you could get away with #8, but with a 50a breaker.
 