I need to provide power for 2 Dry-steem VLC humidifiers. One is 11.1 amps 1 phase, and the other is 14.4 amps 3 phase. The total is 25.5 amps. 125% of this is 32 amps.
I think I need 35A fuses and #10 wire, since article 424.22(D) requires the overcurrent protection and branch circuit conductors to be sized for 125% of the load. (Does this even apply to a humidifier?).
But 240.4(D) requires #8 wire for the 35A fuse. Or does 424.22 overide this?
Steve
I think I need 35A fuses and #10 wire, since article 424.22(D) requires the overcurrent protection and branch circuit conductors to be sized for 125% of the load. (Does this even apply to a humidifier?).
But 240.4(D) requires #8 wire for the 35A fuse. Or does 424.22 overide this?