During my regular journeyman continuing education class last evening, we came upon a calculation problem that was a combination problem. By that I mean that you would have to take into account a number of different code rules and apply them. The instructors were at odds as to what the real answer was, definitively. So was the class of 50 electricians. I brought in one of MH?s books I keep in the car, but it addressed each aspect of the calculation individually, but did not answer the question as a whole. They suggested that if we visit these code discussion groups, we should pose the question. It seems like a no-brainer, and maybe it is. I know the answer I?d use, but I don?t wish to taint your responses.
By the way, this will be my first question or post for a while, and the first to the new board. I have looked for certain people like Andre, but haven?t seen him post up. I have been e-mailed by other collogues suggesting I visit a different board because they re-buff the new format. Well, here goes.
You have a continuous, non-motor load of 47 amps, served by 3 copper conductors in a raceway. A portion of this raceway runs through a boiler room with an ambient of 116 degrees Fahrenheit. Not knowing what type of terminations are in the circuit, what would be the minimum gauge THHN conductor would be allowed by code? [2002 NEC].
I?ll take all your answers back next week. If you visit the other boards, you may see the question worded differently; posted by one the other participants
By the way, this will be my first question or post for a while, and the first to the new board. I have looked for certain people like Andre, but haven?t seen him post up. I have been e-mailed by other collogues suggesting I visit a different board because they re-buff the new format. Well, here goes.
You have a continuous, non-motor load of 47 amps, served by 3 copper conductors in a raceway. A portion of this raceway runs through a boiler room with an ambient of 116 degrees Fahrenheit. Not knowing what type of terminations are in the circuit, what would be the minimum gauge THHN conductor would be allowed by code? [2002 NEC].