hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Please see attach sketch shows ct cabinet with service wire trough.. From the CT cabinet to wire trough have the following:
1. 600kcmil neutral to neutral bar in first service disco
2. 3 sets of 300kcmil neutral to neutral bar in second service disco
3. 3 sets of 300kcmil neutral to neutral bar in third service disco
From the service disco I have the following:
1. Neutral bar from first service disco to terminal bar in wireway #1/0 awg
2. Neutral bar from second service disco to terminal bar in wireway #3/0 awg
3. Neutral bar from third service disco to terminal bar in wireway #3/0 awg
The terminal bar connects to building steel, water pipe each with grounding electrode conductors
The question is wireway must be bonded by neutral NEC 2017 section 250.80 so bonding jumper from terminal bar to the wire way is provided. What size should that bonding jumper be? I am thinking 500kcmil? Yes no? If no then what size?
1. 600kcmil neutral to neutral bar in first service disco
2. 3 sets of 300kcmil neutral to neutral bar in second service disco
3. 3 sets of 300kcmil neutral to neutral bar in third service disco
From the service disco I have the following:
1. Neutral bar from first service disco to terminal bar in wireway #1/0 awg
2. Neutral bar from second service disco to terminal bar in wireway #3/0 awg
3. Neutral bar from third service disco to terminal bar in wireway #3/0 awg
The terminal bar connects to building steel, water pipe each with grounding electrode conductors
The question is wireway must be bonded by neutral NEC 2017 section 250.80 so bonding jumper from terminal bar to the wire way is provided. What size should that bonding jumper be? I am thinking 500kcmil? Yes no? If no then what size?